list Frank Schmerler · Mon, 21 Feb 2011 09:04:47 +0100 ·

Mit freundlichen Grüßen,

Frank Schmerler
Techniker/Projektleiter

Rausch Netzwerktechnik GmbH
Englerstr.26
76275 Ettlingen

Tel: +XX (X)XXXX XXXX-XX
Fax: +XX (X)XXXX XXXX-XX
Web: http://www.rnt.de
HRB  362185
Amtsgericht Mannheim
Geschaeftsfuehrer: Sebastian Nölting
list Nick Camaldi · Wed, 18 May 2011 11:42:01 -0400 ·
Chris has updated his wonderful script that was written for hobbit
##############################
# bb-hosts.cgi
# Written by: Chris Naude
# Purpose: Provides a basic web interface to edit bb-hosts.
#          Uses a lock file and md5sums to keep things sane.
# Requirements: md5sum
# File permissions should be setup so that the web user can write to $xymon_hosts_file
# Hint: Use chmod, chown, setfacl, or sudo. ;)
# Tested on Red Hat AS 3 with Apache2
#
# Version 1.3 - Left justify textarea for IE
#             - Fixed menu
# Version 1.2 - Now supports Xymon 4.3.2 and greater.
# Version 1.1 - Added Xymon support. Enjoy!
#
##############################

go take a look and check out his script section from the menu to view the source

https://cnaude.mdns.org/xymon2-cgi/bb-hosts.cgi
 
Thanks Chris our enviroment uses this alot for multiple pages.
list Venkatesh Subbaramu · Thu, 1 Mar 2012 16:29:30 +0530 ·
Hi All , The xymon counters (like CPU,disk, memory etc ) being monitored for remote server  (2nd server in the list ) is not getting updated .However the server is available .Could you pls suggest dome troubleshooting tips ?


Regards,
Venkatesh


[cid:image001.png at 01CCF7C8.79FE4A90]

**************** CAUTION - Disclaimer *****************
This e-mail contains PRIVILEGED AND CONFIDENTIAL INFORMATION intended solely for the use of the addressee(s). If you are not the intended recipient, please notify the sender by e-mail and delete the original message. Further, you are not to copy, disclose, or distribute this e-mail or its contents to any other person and any such actions are unlawful. This e-mail may contain viruses. Infosys has taken every reasonable precaution to minimize this risk, but is not liable for any damage you may sustain as a result of any virus in this e-mail. You should carry out your own virus checks before opening the e-mail or attachment. Infosys reserves the right to monitor and review the content of all messages sent to or from this e-mail address. Messages sent to or from this e-mail address may be stored on the Infosys e-mail system.
***INFOSYS******** End of Disclaimer ********INFOSYS***
Attachments (1)
list Chris Morris · Fri, 2 Mar 2012 08:51:49 -0000 ·
The xymon client isn't running hence not sending data to the server! Or
the xymon client is running but sending data to the wrong place!


From: xymon-bounces at xymon.com [mailto:xymon-bounces at xymon.com] On Behalf
Of Venkatesh Subbaramu
Sent: 01 March 2012 11:00
To: xymon at xymon.com
Subject: [Xymon] (no subject)
▸ quoted from Venkatesh Subbaramu


	Hi All , The xymon counters (like CPU,disk, memory etc ) being
monitored for remote server  (2nd server in the list ) is not getting
updated .However the server is available .Could you pls suggest dome
troubleshooting tips ?

	 
	Regards,

	Venkatesh

	 
**************************************************************************** 

The information contained in this email is intended only for the use of the intended recipient at the email address to which it has been addressed. If the reader of this message is not an intended recipient, you are hereby notified that you have received this document in error and that any review, dissemination or copying of the message or associated attachments is strictly prohibited. If you have received this email in error, please contact the sender by return email or call 01793 877777 and ask for the sender and then delete it immediately from your system.Please note that neither the RWE Group of Companies nor the sender accepts any responsibility for viruses and it is your responsibility to scan attachments (if any). 

*****************************************************************************
list Venkatesh Subbaramu · Fri, 2 Mar 2012 15:43:10 +0530 ·
Thanks Chris  ! Somebody had changed the bbwin.cfg which was causing the problem .Thanks again for your input .

I did have another question .I have many counters like dbcheck ,xymond ,port which I do not want to display .How can this be hidden ?

Regards,
Venkatesh
▸ quoted from Chris Morris

From: user-e510f6c03e57@xymon.invalid [mailto:user-e510f6c03e57@xymon.invalid]
Sent: Friday, March 02, 2012 2:22 PM
To: Venkatesh Subbaramu
Cc: xymon at xymon.com
Subject: RE: [Xymon] (no subject)

The xymon client isn't running hence not sending data to the server! Or the xymon client is running but sending data to the wrong place!

From: xymon-bounces at xymon.com [mailto:xymon-bounces at xymon.com] On Behalf Of Venkatesh Subbaramu
Sent: 01 March 2012 11:00
To: xymon at xymon.com
Subject: [Xymon] (no subject)
Hi All , The xymon counters (like CPU,disk, memory etc ) being monitored for remote server  (2nd server in the list ) is not getting updated .However the server is available .Could you pls suggest dome troubleshooting tips ?


Regards,
Venkatesh


****************************************************************************

The information contained in this email is intended only for the use of the intended recipient at the email address to which it has been addressed. If the reader of this message is not an intended recipient, you are hereby notified that you have received this document in error and that any review, dissemination or copying of the message or associated attachments is strictly prohibited. If you have received this email in error, please contact the sender by return email or call 01793 877777 and ask for the sender and then delete it immediately from your system.Please note that neither the RWE Group of Companies nor the sender accepts any responsibility for viruses and it is your responsibility to scan attachments (if any).


*****************************************************************************


**************** CAUTION - Disclaimer *****************
This e-mail contains PRIVILEGED AND CONFIDENTIAL INFORMATION intended solely for the use of the addressee(s). If you are not the intended recipient, please notify the sender by e-mail and delete the original message. Further, you are not to copy, disclose, or distribute this e-mail or its contents to any other person and any such actions are unlawful. This e-mail may contain viruses. Infosys has taken every reasonable precaution to minimize this risk, but is not liable for any damage you may sustain as a result of any virus in this e-mail. You should carry out your own virus checks before opening the e-mail or attachment. Infosys reserves the right to monitor and review the content of all messages sent to or from this e-mail address. Messages sent to or from this e-mail address may be stored on the Infosys e-mail system.
***INFOSYS******** End of Disclaimer ********INFOSYS***
list Martin Flemming · Fri, 2 Mar 2012 11:19:13 +0100 (CET) ·
▸ quoted from Venkatesh Subbaramu

On Fri, 2 Mar 2012, Venkatesh Subbaramu wrote:
Thanks Chris  ! Somebody had changed the bbwin.cfg which was causing the problem .Thanks again for your input .

 

I did have another question .I have many counters like dbcheck ,xymond ,port which I do not want to display .How can this be hidden ?
General, you put only the test you want to see with

group-only in your host.cfg

http://www.xymon.com/xymon/help/manpages/man5/hosts.cfg.5.html

group-only COLUMN1|COLUMN2|COLUMN3 [group-title]
     Same as the "group" and "group-compress" lines, but includes only the 
columns explicitly listed in the group. Any columns not listed will be 
ignored for these hosts.

cheers,
 	martin
▸ quoted from Venkatesh Subbaramu

 

Regards,

Venkatesh

 

From: user-e510f6c03e57@xymon.invalid [mailto:user-e510f6c03e57@xymon.invalid]
Sent: Friday, March 02, 2012 2:22 PM
To: Venkatesh Subbaramu
Cc: xymon at xymon.com
Subject: RE: [Xymon] (no subject)

 

The xymon client isn't running hence not sending data to the server! Or the xymon client is running but sending data to the wrong place!

 


From: xymon-bounces at xymon.com [mailto:xymon-bounces at xymon.com] On Behalf Of Venkatesh Subbaramu
Sent: 01 March 2012 11:00
To: xymon at xymon.com
Subject: [Xymon] (no subject)

      Hi All , The xymon counters (like CPU,disk, memory etc ) being monitored for remote server  (2nd server in the list ) is not getting
      updated .However the server is available .Could you pls suggest dome troubleshooting tips ?

       

       

      Regards,

      Venkatesh

       

****************************************************************************

The information contained in this email is intended only for the use of the intended recipient at the email address to which it has been addressed.
If the reader of this message is not an intended recipient, you are hereby notified that you have received this document in error and that any
review, dissemination or copying of the message or associated attachments is strictly prohibited. If you have received this email in error, please
contact the sender by return email or call 01793 877777 and ask for the sender and then delete it immediately from your system.Please note that
neither the RWE Group of Companies nor the sender accepts any responsibility for viruses and it is your responsibility to scan attachments (if any).

 

*****************************************************************************

 

**************** CAUTION - Disclaimer *****************
This e-mail contains PRIVILEGED AND CONFIDENTIAL INFORMATION intended solely
for the use of the addressee(s). If you are not the intended recipient, please
notify the sender by e-mail and delete the original message. Further, you are not
to copy, disclose, or distribute this e-mail or its contents to any other person and
any such actions are unlawful. This e-mail may contain viruses. Infosys has taken
every reasonable precaution to minimize this risk, but is not liable for any damage
you may sustain as a result of any virus in this e-mail. You should carry out your
own virus checks before opening the e-mail or attachment. Infosys reserves the
right to monitor and review the content of all messages sent to or from this e-mail
address. Messages sent to or from this e-mail address may be stored on the
Infosys e-mail system.
***INFOSYS******** End of Disclaimer ********INFOSYS***
list Chris Morris · Fri, 2 Mar 2012 10:21:17 -0000 ·
use the :-
 
group-except COLUMN1|COLUMN2|COLUMN3 [group-title] 
Same as the "group-only" lines, but includes all columns EXCEPT those
explicitly listed in the group. Any columns listed will be ignored for
these hosts - all other columns are shown. 
 
in hosts.cfg on the xymon server.
 
Try reading the xymon help pages or man pages before posting here -
these are really basic questions.
▸ quoted from Venkatesh Subbaramu
 

	From: Venkatesh Subbaramu [mailto:user-836ee4520eff@xymon.invalid] 
	Sent: 02 March 2012 10:13
	To: Morris, Chris (SS-IS)
	Cc: xymon at xymon.com
	Subject: RE: [Xymon] (no subject)
	
	
	Thanks Chris  ! Somebody had changed the bbwin.cfg which was
causing the problem .Thanks again for your input .

	 
	I did have another question .I have many counters like dbcheck
,xymond ,port which I do not want to display .How can this be hidden ?

	 
	Regards,

	Venkatesh

	 
	From: user-e510f6c03e57@xymon.invalid [mailto:user-e510f6c03e57@xymon.invalid] 
	Sent: Friday, March 02, 2012 2:22 PM
	To: Venkatesh Subbaramu
	Cc: xymon at xymon.com
	Subject: RE: [Xymon] (no subject)

	 
	The xymon client isn't running hence not sending data to the
server! Or the xymon client is running but sending data to the wrong
place!

	 
	From: xymon-bounces at xymon.com [mailto:xymon-bounces at xymon.com]
On Behalf Of Venkatesh Subbaramu
	Sent: 01 March 2012 11:00
	To: xymon at xymon.com
	Subject: [Xymon] (no subject)

		Hi All , The xymon counters (like CPU,disk, memory etc )
being monitored for remote server  (2nd server in the list ) is not
getting updated .However the server is available .Could you pls suggest
dome troubleshooting tips ?

		 
		Regards,

		Venkatesh

		 
************************************************************************
**** 

	The information contained in this email is intended only for the
use of the intended recipient at the email address to which it has been
addressed. If the reader of this message is not an intended recipient,
you are hereby notified that you have received this document in error
and that any review, dissemination or copying of the message or
associated attachments is strictly prohibited. If you have received this
email in error, please contact the sender by return email or call 01793
877777 and ask for the sender and then delete it immediately from your
system.Please note that neither the RWE Group of Companies nor the
sender accepts any responsibility for viruses and it is your
responsibility to scan attachments (if any). 

	 
************************************************************************
***** 

	 
**************** CAUTION - Disclaimer *****************
This e-mail contains PRIVILEGED AND CONFIDENTIAL INFORMATION intended
solely 
for the use of the addressee(s). If you are not the intended recipient,
please 
notify the sender by e-mail and delete the original message. Further,
you are not 
to copy, disclose, or distribute this e-mail or its contents to any
other person and 
any such actions are unlawful. This e-mail may contain viruses. Infosys
has taken 
every reasonable precaution to minimize this risk, but is not liable for
any damage 
you may sustain as a result of any virus in this e-mail. You should
carry out your 
own virus checks before opening the e-mail or attachment. Infosys
reserves the 
right to monitor and review the content of all messages sent to or from
this e-mail 
address. Messages sent to or from this e-mail address may be stored on
the 
Infosys e-mail system.
***INFOSYS******** End of Disclaimer ********INFOSYS***


**************************************************************************** 
The information contained in this email is intended only for the use of the intended recipient at the email address to which it has been addressed. If the reader of this message is not an intended recipient, you are hereby notified that you have received this document in error and that any review, dissemination or copying of the message or associated attachments is strictly prohibited. If you have received this email in error, please contact the sender by return email or call 01793 877777 and ask for the sender and then delete it immediately from your system.Please note that neither the RWE Group of Companies nor the sender accepts any responsibility for viruses and it is your responsibility to scan attachments (if any). 

*****************************************************************************
list Venkatesh Subbaramu · Fri, 2 Mar 2012 16:06:23 +0530 ·
Thank You!


-----Original Message-----
From: xymon-bounces at xymon.com [mailto:xymon-bounces at xymon.com] On Behalf Of Martin Flemming
Sent: Friday, March 02, 2012 3:49 PM
To: xymon at xymon.com
Subject: Re: [Xymon] (no subject)


On Fri, 2 Mar 2012, Venkatesh Subbaramu wrote:
Thanks Chris  ! Somebody had changed the bbwin.cfg which was causing the problem .Thanks again for your input .

 

I did have another question .I have many counters like dbcheck ,xymond ,port which I do not want to display .How can this be hidden ?
General, you put only the test you want to see with

group-only in your host.cfg

http://www.xymon.com/xymon/help/manpages/man5/hosts.cfg.5.html

group-only COLUMN1|COLUMN2|COLUMN3 [group-title]
     Same as the "group" and "group-compress" lines, but includes only the columns explicitly listed in the group. Any columns not listed will be ignored for these hosts.

cheers,
 	martin

 

Regards,

Venkatesh

 

From: user-e510f6c03e57@xymon.invalid [mailto:user-e510f6c03e57@xymon.invalid]
Sent: Friday, March 02, 2012 2:22 PM
To: Venkatesh Subbaramu
Cc: xymon at xymon.com
Subject: RE: [Xymon] (no subject)

 

The xymon client isn't running hence not sending data to the server! Or the xymon client is running but sending data to the wrong place!

 


From: xymon-bounces at xymon.com [mailto:xymon-bounces at xymon.com] On Behalf Of Venkatesh Subbaramu
Sent: 01 March 2012 11:00
To: xymon at xymon.com
Subject: [Xymon] (no subject)

      Hi All , The xymon counters (like CPU,disk, memory etc ) being monitored for remote server  (2nd server in the list ) is not getting
      updated .However the server is available .Could you pls suggest dome troubleshooting tips ?

       

       

      Regards,

      Venkatesh

       

**********************************************************************
******

The information contained in this email is intended only for the use of the intended recipient at the email address to which it has been addressed.
If the reader of this message is not an intended recipient, you are hereby notified that you have received this document in error and that any review, dissemination or copying of the message or associated attachments is strictly prohibited. If you have received this email in error, please contact the sender by return email or call 01793 877777 and ask for the sender and then delete it immediately from your system.Please note that neither the RWE Group of Companies nor the sender accepts any responsibility for viruses and it is your responsibility to scan attachments (if any).

 

**********************************************************************
*******

 

**************** CAUTION - Disclaimer ***************** This e-mail contains PRIVILEGED AND CONFIDENTIAL INFORMATION intended solely for the use of the addressee(s). If you are not the intended recipient, please notify the sender by e-mail and delete the original message. Further, you are not to copy, disclose, or distribute this e-mail or its contents to any other person and any such actions are unlawful. This e-mail may contain viruses. Infosys has taken every reasonable precaution to minimize this risk, but is not liable for any damage you may sustain as a result of any virus in this e-mail. You should carry out your own virus checks before opening the e-mail or attachment. Infosys reserves the right to monitor and review the content of all messages sent to or from this e-mail address. Messages sent to or from this e-mail address may be stored on the Infosys e-mail system.
***INFOSYS******** End of Disclaimer ********INFOSYS***
list Martin Ward · Fri, 2 Mar 2012 14:37:11 +0000 ·
All the purple entries come from the client itself so I would recommend that you ensure that the Xymon or Hobbit client is running properly on “infy-x08vcanbsp” and that it can reach the Xymon server on port 1984.

|\/|artin
▸ quoted from Venkatesh Subbaramu

From: xymon-bounces at xymon.com [mailto:xymon-bounces at xymon.com] On Behalf Of Venkatesh Subbaramu
Sent: 01 March 2012 11:59
To: xymon at xymon.com
Subject: [Xymon] (no subject)

Hi All , The xymon counters (like CPU,disk, memory etc ) being monitored for remote server  (2nd server in the list ) is not getting updated .However the server is available .Could you pls suggest dome troubleshooting tips ?


Regards,
Venkatesh


[cid:image001.png at 01CCF859.96DA2BC0]
▸ quoted from Venkatesh Subbaramu

**************** CAUTION - Disclaimer *****************

This e-mail contains PRIVILEGED AND CONFIDENTIAL INFORMATION intended solely

for the use of the addressee(s). If you are not the intended recipient, please

notify the sender by e-mail and delete the original message. Further, you are not

to copy, disclose, or distribute this e-mail or its contents to any other person and

any such actions are unlawful. This e-mail may contain viruses. Infosys has taken

every reasonable precaution to minimize this risk, but is not liable for any damage

you may sustain as a result of any virus in this e-mail. You should carry out your

own virus checks before opening the e-mail or attachment. Infosys reserves the

right to monitor and review the content of all messages sent to or from this e-mail

address. Messages sent to or from this e-mail address may be stored on the

Infosys e-mail system.

***INFOSYS******** End of Disclaimer ********INFOSYS***


[Colt Disclaimer]
The message is intended for the named addressee only and may not be disclosed
to or used by anyone else, nor may it be copied in any way. The contents of
this message and its attachments are confidential and may also be subject to
legal privilege. If you are not the named addressee and/or have received this
message in error, please advise us by e-mailing user-51905b889b93@xymon.invalid and delete the
message and any attachments without retaining any copies. Internet
communications are not secure and Colt does not accept responsibility for this
message, its contents nor responsibility for any viruses. No contracts can be
created or varied on behalf of Colt Technology Services, its subsidiaries,
group companies or affiliates ("Colt") and any other party by email
communications unless expressly agreed in writing with such other party.
Please note that incoming emails will be automatically scanned to eliminate
potential viruses and unsolicited promotional emails. For more information
refer to www.colt.net or contact us on +44(0)20 7390 3900
list Randy Shults · Thu, 7 Jun 2012 17:05:39 -0400 ·
list Akshar Bhosale · Mon, 6 Aug 2012 01:11:04 +0530 ·
i am getting following error on rhel 5.2 server running xymon 4.2.2
and now devmon-0.3.1-beta1 for the first time

./devmon --readbbhosts
[12-08-06 at 01:01:43] No matching templates for device: svr2-test

if i do

snmpwalk -v2c -c public svr2-test  ,i get
SNMPv2-MIB::sysDescr.0 = STRING: Linux svr2-test 2.6.18-128.el5 #1 SMP
Wed Dec 17 11:41:38 EST 2008 x86_64

i hv created one template file

cat templates/svr2-test
vendor : HP
model : HP server
snmpver : 2
sysdesc : 2.6.18-128.el5


following is bb-hosts entry..

192.168.0.110    svr2-test   #ssh DEVMON:cid(public)


pl let me know wt is wrong?
list Colin Coe · Mon, 10 Mar 2014 06:38:38 +0800 ·
Hi all

Server info:
Host - RHEL6.5
Version - 4.3.17
Packaged by J Cleaver (Terabithia)

I'm having a problem with a definition in /etc/xymon/client-local.cfg.
---
[host=dmz_ap01]
file:`ls -ltr /home/enmac/customer-data/CUST9100REP*CSV | tail -n 1`
---
The problem is that Xymon reports bad (red) with the page showing
---
 -rw-r--r-- 1 username groupname14314345 Mar 10  2014
/home/username/customer-data/CUST9100REP20140310002349.CSV
File is missing
---
Now, the file is not missing, and Xymon is correctly showing its mode,
size, ownership details, etc.
Any ideas what I've done wrong here?

Thanks

CC

-- 
RHCE#805007969328369
list Jeremy Laidman · Sat, 15 Mar 2014 09:38:06 +1100 ·
On 10 March 2014 09:38, Colin Coe <user-5b250cd7a540@xymon.invalid> wrote:
file:`ls -ltr /home/enmac/customer-data/CUST9100REP*CSV | tail -n 1`
Xymon requires that the filename is produced by the backticks.  You're
having it produce more than the filename because you have the "-l" switch
for the "ls" command.  Try:

file:`ls -tr /home/enmac/customer-data/CUST9100REP*CSV | tail -n 1`

J
list Michael Resnick · Wed, 2 Jul 2014 06:48:48 -0700 ·
xymon-client on xymon server sending to other xymon servers    


I have this working in one environment with 3 xymon servers, but just set up another 2 servers in a locked down environment.

To have data sent to other xymon servers, all I had to do was change the 

XYMSERVERS=
line in xymonclient.cfg in the /home/xymon/client/etc folder


Running 4.3.11 in my normal setup, and 4.3.10 in the new one. RHEL 6 in the new setup and Centos 5 in the old one.

I am not seeing anything from the either new server in ghost client report except
 
 
10.24.13.31    jsppvlscix01    1:16  , with a blank hostname

, or in the defined server in hosts.cfg. 
ping is working between the 2 new servers.

Is there anything else that needs to be done for the xymon client to work on the xymon server ?
I checked my working and new tasks.cfg and they appear to be the same.
I also checked that port 1984 is open on each via telnet.

Any hints appreciated on how to do further testing. 


Thanks !
list Alvarez Aguilar José Trinidad · Wed, 27 Aug 2014 19:54:08 -0500 ·
Hello.

Engineers where I can find a script that allows me to monitor HP Proliant DL360 equipment windows, specifcally the hardware (drives, voltage, memory, power supplies, etc.). Xymon server is a computer running solaris 9 operating system.

Thank you.


José Trinidad Álvarez Aguilar
Av. Epigmenio Gonzalez No. 2, Col. Parques Industriales, C:P.76150
Santiago de Querétaro, Qro.
Tel. 101-82-31

[cid:image001.jpg at 01CFC230.66C132F0]


 [cid:GWR_ALDEA-01.jpg]

CONFIDENTIALITY NOTICE:

This e-mail message including attachments, if any, is intended only for the person or entity to which it is addressed and may contain confidential and /or privileged material. Any review, use, disclosure or distribution of such confidential information without the written authorization of Teléfonos de México is prohibited. If you are not the intended recipient, please contact the sender by reply e-mail and destroy all copies of the original message. By receiving this e-mail you acknowledge that any breach by you and/or your representatives of the above provisions may entitle Teléfonos de México to seek for damages.

 
AVISO DE CONFIDENCIALIDAD:

Este correo electrónico, incluyendo en su caso, los archivos adjuntos al mismo, pueden contener información de carácter confidencial y/o privilegiada, y se envían a la atención única y exclusivamente de la persona y/o entidad a quien va dirigido. La copia, revisión, uso, revelación y/o distribución de dicha información confidencial sin la autorización por escrito de Teléfonos de México está prohibida. Si usted no es el destinatario a quien se dirige el presente correo, favor de contactar al remitente respondiendo al presente correo y eliminar el correo original incluyendo sus archivos, así como cualesquiera copia del mismo. Mediante la recepción del presente correo usted reconoce y acepta que en caso de incumplimiento de su parte y/o de sus representantes a los términos antes mencionados, Teléfonos de México tendrá derecho a los daños y perjuicios que esto le cause.
Attachments (1)
list Torkil Zachariassen · Thu, 17 Mar 2016 18:47:59 +0000 ·
On our xymon (4.3.26) server, which otherwise works just fine,
/var/log/xymon/xymonlaunch.log issues the following warning the
following every 5 minutes.
This again indicates that the culprit is xymonlaunch
:

WARNING: Cannot open include file '/var/run/xymonclient-runtime.cfg',
line was: include /var/run/xymonclient-runtime.cfg

This seems related to an earlier report  @
http://comments.gmane.org/gmane.comp.monitoring.hobbit/26155  stating

" that in: /usr/lib/xymon/client/etc/xymonclient.cfg on the server
once the RPM is
installed you need to replace the include statement with the below text:
XYMSRV=""          # IP address of the Xymon server
XYMSERVERS=""                   # IP of multiple Xymon servers. XYMSRV
must be "0.0.0.0".

This is because the init script for the client correctly uses the
/etc/default/xymon-client to create a
file /var/run/xymonclient-runtime.cfg that is what is included, but
the server init script does not do these things."


I suppose there are multiple ways to resolve this, but some advice is needed:
1) include a few line into the server init script (/etc/init.d/xymon)
which creates the xymonclients-runtime.cfg file
2) modify or remove the include line in
/usr/lib/xymon/client/etc/xymonclient.cfg on the server

We use rpms created from the supplied spec files, and the server has
the xymon package installed only, as the xymon(-server) and
xymon-client packages conflicts (you can not install both)

For now we have commented the include line out manually, but please
advise on what a proper resolution might look like.

regards
...torkil...
list Jeremy Laidman · Tue, 22 Mar 2016 00:04:26 +0000 ·
Torkil

I recommend you put subjects in your posts, which will not only increase
engagement, but also helps with searching the archives.

On Fri, Mar 18, 2016 at 7:59 AM Torkil Zachariassen <
▸ quoted from Torkil Zachariassen
user-1cb1ab48e1ec@xymon.invalid> wrote:
On our xymon (4.3.26) server, which otherwise works just fine,
/var/log/xymon/xymonlaunch.log issues the following warning the
following every 5 minutes.
This again indicates that the culprit is xymonlaunch
:

WARNING: Cannot open include file '/var/run/xymonclient-runtime.cfg',
line was: include /var/run/xymonclient-runtime.cfg

This seems related to an earlier report  @
http://comments.gmane.org/gmane.comp.monitoring.hobbit/26155  stating
<snip>

I suppose there are multiple ways to resolve this, but some advice is
needed:
1) include a few line into the server init script (/etc/init.d/xymon)
which creates the xymonclients-runtime.cfg file
2) modify or remove the include line in
/usr/lib/xymon/client/etc/xymonclient.cfg on the server
On my installation, I have this in /etc/default/xymon:

cat <<EOF >/var/run/xymonclient-runtime.cfg
XYMSERVERS="10.3.3.20 10.3.23.20"
XYMSRV="0.0.0.0"
EOF

(Note: I have two xymon servers, hence two IP addresses.)

This automatically creates the /var/run/xymonclient-runtime.cfg file each
time the Xymon server is started using the init scripts.  Not sure if this
is the best way, or even a very good way.  But it works for me.

The thing is, files in /var/run/ probably shouldn't be expected to exist
after a reboot.  In practice, I suspect they do for most apps, but a system
administrator should be able to wipe this directory out prior to a reboot,
and everything should come back like it was before.
▸ quoted from Torkil Zachariassen

We use rpms created from the supplied spec files, and the server has
the xymon package installed only, as the xymon(-server) and
xymon-client packages conflicts (you can not install both)

For now we have commented the include line out manually, but please
advise on what a proper resolution might look like.

Have you restarted Xymon since doing this?  Do the client scripts work as
expected?

I suspect that if you remove the include line altogether, you will no
longer have XYMSERVERS/XYMSRV defined, and it will break the client side on
next restart.  (Actually, it might even cause impact on the next execution
of xymonclient, typically every 5 minutes.)  If this is the case, you would
have to replace the include line either with definitions of these
variables, or an include for a different file, which you populate with the
values you require.

I don't know the "correct" way to do this kind of thing.  There's certainly
a problem here, where the default install creates errors in the logs.  It'd
be good to get some input from any of the guys on the list who were
involved in creating the spec.

J
list Robert Schetterer · Mon, 30 Sep 2019 18:05:00 +0200 ·
Hi, what default checks need lsof
can these be disabled ?

-- 
[*] sys4 AG

http://sys4.de, +49 (89) 30 90 46 64
Schlei?heimer Stra?e 26/MG, 80333 M?nchen

Sitz der Gesellschaft: M?nchen, Amtsgericht M?nchen: HRB 199263
Vorstand: Patrick Ben Koetter, Marc Schiffbauer
Aufsichtsratsvorsitzender: Florian Kirstein
list Thomas Eckert · Mon, 30 Sep 2019 19:50:43 +0200 ·
Hi Robert,
I'm not aware of any xymon-default using 'lsof'. Where do you see it being called/used?

Cheers
Thomas

▸ quoted from Robert Schetterer
On Sep 30, 2019 18:05, Robert Schetterer wrote:

Hi, what default checks need lsof
can these be disabled ?

--
[*] sys4 AG

http://sys4.de, +49 (89) 30 90 46 64

Schleißheimer Straße 26/MG, 80333 München

Sitz der Gesellschaft: München, Amtsgericht München: HRB 199263
Vorstand: Patrick Ben Koetter, Marc Schiffbauer
Aufsichtsratsvorsitzender: Florian Kirstein

Xymon@xymon.com

list Thomas Eckert · Tue, 1 Oct 2019 09:07:11 +0200 ·
apologies for re-sending - subject on previous post got lost
▸ quoted from Thomas Eckert

Hi Robert,
I'm not aware of any xymon-default using 'lsof'. Where do you see it being called/used?

If you have extensions, e.g. the `hobbit-plugins`-package present in Debian, this changes of course.
The `libs`-extension included in that package for instance uses `lsof`.

All the best
Thomas
▸ quoted from Robert Schetterer
On 30 Sep 2019, at 18:05, Robert Schetterer <user-4fb463f4125a@xymon.invalid> wrote:

Hi, what default checks need lsof
can these be disabled ?

-- 
[*] sys4 AG

http://sys4.de, +49 (89) 30 90 46 64
Schlei?heimer Stra?e 26/MG, 80333 M?nchen

Sitz der Gesellschaft: M?nchen, Amtsgericht M?nchen: HRB 199263
Vorstand: Patrick Ben Koetter, Marc Schiffbauer
Aufsichtsratsvorsitzender: Florian Kirstein
list Robert Schetterer · Tue, 1 Oct 2019 13:28:48 +0200 ·
Am 01.10.2019 um 09:07 schrieb Thomas Eckert:
▸ quoted from Thomas Eckert
apologies for re-sending - subject on previous post got lost

Hi Robert,
I'm not aware of any xymon-default using 'lsof'. Where do you see it being called/used?

If you have extensions, e.g. the `hobbit-plugins`-package present in Debian, this changes of course.
The `libs`-extension included in that package for instance uses `lsof`.
Hi , yes it should be libs extension
thx so far

Robert
▸ quoted from Thomas Eckert
All the best
Thomas
On 30 Sep 2019, at 18:05, Robert Schetterer <user-4fb463f4125a@xymon.invalid> wrote:

Hi, what default checks need lsof
can these be disabled ?

-- 
[*] sys4 AG

http://sys4.de, +49 (89) 30 90 46 64
Schlei?heimer Stra?e 26/MG, 80333 M?nchen

Sitz der Gesellschaft: M?nchen, Amtsgericht M?nchen: HRB 199263
Vorstand: Patrick Ben Koetter, Marc Schiffbauer
Aufsichtsratsvorsitzender: Florian Kirstein
-- 

[*] sys4 AG

https://sys4.de, +49 (89) 30 90 46 64
Schlei?heimer Stra?e 26/MG,80333 M?nchen

Sitz der Gesellschaft: M?nchen, Amtsgericht M?nchen: HRB 199263
Vorstand: Patrick Ben Koetter, Marc Schiffbauer, Wolfgang Stief
Aufsichtsratsvorsitzender: Florian Kirstein
list Jesus Hornelas · Mon, 7 Mar 2022 13:29:38 -0600 ·
 Good afternoon
It is not displaying the event history in the xymon it sends the following
message

Historical status log not available

It is not generating the event logs, I already checked the xymon path on
the server and there is no file, for some reason it is not being generated.
any suggestion please !!!