Xymon Mailing List Archive search

Client uptime status is failing

13 messages in this thread

list Devvkanth Krishnamurthy · Tue, 29 Jan 2019 11:06:01 +0000 ·
Hi,
I am having trouble w.r.t to uptime status generation in clients. The server is displaying uptime correctly since xymond fetches the data, whereas for the clients it does not fetch the uptime data. However it populates all other columns. Can you please suggest if I am missing anything here.

Situation :

Xymon server  and Xymon clients are  configured. The table is populated with colors and data being generated except for uptime in clients whereas the server is reporting uptime correctly. This is probably because of xymond daemon. The status message also indicated service not available which indicates xymond service.  So how can we get the Xymon clients to  update the uptime.

Tasks.cfg file :

# The client back-end module. You need this if you are running the Xymon client on any system.
[clientdata]
        ENVFILE /home/xymon/server/etc/xymonserver.cfg
        NEEDS xymond
        CMD xymond_channel --channel=client --log=$XYMONSERVERLOGS/clientdata.log xymond_client --uptime-status

Status message :

[cid:image001.png at 01D4B7F0.49E78250]


Thanks and Regards,
Devvkanth K
Unix SME
list Sebastian Auriol · Tue, 29 Jan 2019 11:47:03 +0000 ·
This may be down to what your clients are reporting.  What client
version(s) are you talking about here?

Kind regards,

SebA


On Tue, 29 Jan 2019 at 11:06, Devvkanth Krishnamurthy <
▸ quoted from Devvkanth Krishnamurthy
user-8a837177683f@xymon.invalid> wrote:
Hi,

I am having trouble w.r.t to uptime status generation in clients. The
server is displaying uptime correctly since xymond fetches the data,
whereas for the clients it does not fetch the uptime data. However it
populates all other columns. Can you please suggest if I am missing
anything here.


*Situation* :


Xymon server  and Xymon clients are  configured. The table is populated
with colors and data being generated except for uptime in clients whereas
the server is reporting uptime correctly. This is probably because of
xymond daemon. The status message also indicated service not available
which indicates xymond service.  So how can we get the Xymon clients to
update the uptime.


*Tasks.cfg file :*


# The client back-end module. You need this if you are running the Xymon
client on any system.

[clientdata]

        ENVFILE /home/xymon/server/etc/xymonserver.cfg

        NEEDS xymond

        CMD xymond_channel --channel=client
--log=$XYMONSERVERLOGS/clientdata.log xymond_client --uptime-status


*Status message :*


Thanks and Regards,

Devvkanth K

Unix SME

list Devvkanth Krishnamurthy · Tue, 29 Jan 2019 12:14:34 +0000 ·
Hi,

I have Xymon version – 4.3.28 for both server and clients.
▸ quoted from Sebastian Auriol

Thanks and Regards,
Devvkanth K
Unix SME

From: SebA <user-4631430d620a@xymon.invalid>
Sent: Tuesday, January 29, 2019 5:17 PM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
Cc: xymon at xymon.com
Subject: Re: [Xymon] Client uptime status is failing

This may be down to what your clients are reporting.  What client version(s) are you talking about here?

Kind regards,

SebA


On Tue, 29 Jan 2019 at 11:06, Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi,
I am having trouble w.r.t to uptime status generation in clients. The server is displaying uptime correctly since xymond fetches the data, whereas for the clients it does not fetch the uptime data. However it populates all other columns. Can you please suggest if I am missing anything here.

Situation :

Xymon server  and Xymon clients are  configured. The table is populated with colors and data being generated except for uptime in clients whereas the server is reporting uptime correctly. This is probably because of xymond daemon. The status message also indicated service not available which indicates xymond service.  So how can we get the Xymon clients to  update the uptime.

Tasks.cfg file :

# The client back-end module. You need this if you are running the Xymon client on any system.
[clientdata]
        ENVFILE /home/xymon/server/etc/xymonserver.cfg
        NEEDS xymond
        CMD xymond_channel --channel=client --log=$XYMONSERVERLOGS/clientdata.log xymond_client --uptime-status

Status message :

[cid:image001.png at 01D4B7FA.46FC16A0]


Thanks and Regards,
Devvkanth K
Unix SME
list Devvkanth Krishnamurthy · Mon, 4 Feb 2019 16:09:56 +0000 ·
Hi,

Do you mind giving any suggestions on why only the Xymon server uptime is reporting correctly whereas the client says that service is unavailable. Not sure what I am missing here.
▸ quoted from Devvkanth Krishnamurthy

Thanks and Regards,
Devvkanth K
Unix SME

From: Devvkanth Krishnamurthy
Sent: Tuesday, January 29, 2019 5:45 PM
To: SebA <user-4631430d620a@xymon.invalid>
Cc: xymon at xymon.com
Subject: RE: [Xymon] Client uptime status is failing

Hi,

I have Xymon version – 4.3.28 for both server and clients.

Thanks and Regards,
Devvkanth K
Unix SME

From: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>
Sent: Tuesday, January 29, 2019 5:17 PM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>>
Cc: xymon at xymon.com<mailto:xymon at xymon.com>
Subject: Re: [Xymon] Client uptime status is failing

This may be down to what your clients are reporting.  What client version(s) are you talking about here?

Kind regards,

SebA


On Tue, 29 Jan 2019 at 11:06, Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi,
I am having trouble w.r.t to uptime status generation in clients. The server is displaying uptime correctly since xymond fetches the data, whereas for the clients it does not fetch the uptime data. However it populates all other columns. Can you please suggest if I am missing anything here.

Situation :

Xymon server  and Xymon clients are  configured. The table is populated with colors and data being generated except for uptime in clients whereas the server is reporting uptime correctly. This is probably because of xymond daemon. The status message also indicated service not available which indicates xymond service.  So how can we get the Xymon clients to  update the uptime.

Tasks.cfg file :

# The client back-end module. You need this if you are running the Xymon client on any system.
[clientdata]
        ENVFILE /home/xymon/server/etc/xymonserver.cfg
        NEEDS xymond
        CMD xymond_channel --channel=client --log=$XYMONSERVERLOGS/clientdata.log xymond_client --uptime-status

Status message :

[cid:image001.png at 01D4BCD1.8417B540]


Thanks and Regards,
Devvkanth K
Unix SME
list Sebastian Auriol · Mon, 4 Feb 2019 19:27:34 +0000 ·
I've never seen that before - have you added uptime to hosts.cfg?  If so,
remove it!  (It looks like the Xymon server is testing a network service
here, and uptime is not a network service!)

Kind regards,

SebA


On Mon, 4 Feb 2019 at 16:10, Devvkanth Krishnamurthy <
▸ quoted from Devvkanth Krishnamurthy
user-8a837177683f@xymon.invalid> wrote:
Hi,


Do you mind giving any suggestions on why only the Xymon server uptime is
reporting correctly whereas the client says that service is unavailable.
Not sure what I am missing here.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* Devvkanth Krishnamurthy
*Sent:* Tuesday, January 29, 2019 5:45 PM
*To:* SebA <user-4631430d620a@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* RE: [Xymon] Client uptime status is failing


Hi,


I have Xymon version – 4.3.28 for both server and clients.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* SebA <user-4631430d620a@xymon.invalid>
*Sent:* Tuesday, January 29, 2019 5:17 PM
*To:* Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* Re: [Xymon] Client uptime status is failing


This may be down to what your clients are reporting.  What client
version(s) are you talking about here?


Kind regards,

SebA


On Tue, 29 Jan 2019 at 11:06, Devvkanth Krishnamurthy <
user-8a837177683f@xymon.invalid> wrote:

Hi,

I am having trouble w.r.t to uptime status generation in clients. The
server is displaying uptime correctly since xymond fetches the data,
whereas for the clients it does not fetch the uptime data. However it
populates all other columns. Can you please suggest if I am missing
anything here.


*Situation* :


Xymon server  and Xymon clients are  configured. The table is populated
with colors and data being generated except for uptime in clients whereas
the server is reporting uptime correctly. This is probably because of
xymond daemon. The status message also indicated service not available
which indicates xymond service.  So how can we get the Xymon clients to
update the uptime.


*Tasks.cfg file :*


# The client back-end module. You need this if you are running the Xymon
client on any system.

[clientdata]

        ENVFILE /home/xymon/server/etc/xymonserver.cfg

        NEEDS xymond

        CMD xymond_channel --channel=client
--log=$XYMONSERVERLOGS/clientdata.log xymond_client --uptime-status


*Status message :*


Thanks and Regards,

Devvkanth K

Unix SME


<https://apac01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.xymon.com%2Fmailman%2Flistinfo%2Fxymon&data=user-77322baadbba@xymon.invalid%7C39d54149bbca434c576808d685dfacc1%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636843593077828551&sdata=vgfSmqopsssBkwdBS4ANlYDf6SjU6UNrtCBr7Yte4Gc%3D&reserved=0>;

list Devvkanth Krishnamurthy · Thu, 7 Feb 2019 12:08:08 +0000 ·
Hi,

I have removed the uptime from hosts.cfg file and  --uptime-status is inserted in tasks.cfg. yet I do not see the uptime column in it . Please check below, I have tried all the resolution available on the net, but I m not able to figure this one out.

[cid:image002.png at 01D4BF0B.B785C610]
▸ quoted from Sebastian Auriol

Thanks and Regards,
Devvkanth K
Unix SME

From: SebA <user-4631430d620a@xymon.invalid>
Sent: Tuesday, February 5, 2019 12:58 AM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
Cc: xymon at xymon.com
Subject: Re: [Xymon] Client uptime status is failing

I've never seen that before - have you added uptime to hosts.cfg?  If so, remove it!  (It looks like the Xymon server is testing a network service here, and uptime is not a network service!)

Kind regards,

SebA


On Mon, 4 Feb 2019 at 16:10, Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi,

Do you mind giving any suggestions on why only the Xymon server uptime is reporting correctly whereas the client says that service is unavailable. Not sure what I am missing here.

Thanks and Regards,
Devvkanth K
Unix SME

From: Devvkanth Krishnamurthy
Sent: Tuesday, January 29, 2019 5:45 PM
To: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>
Cc: xymon at xymon.com<mailto:xymon at xymon.com>
Subject: RE: [Xymon] Client uptime status is failing

Hi,

I have Xymon version – 4.3.28 for both server and clients.

Thanks and Regards,
Devvkanth K
Unix SME

From: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>
Sent: Tuesday, January 29, 2019 5:17 PM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>>
Cc: xymon at xymon.com<mailto:xymon at xymon.com>
Subject: Re: [Xymon] Client uptime status is failing

This may be down to what your clients are reporting.  What client version(s) are you talking about here?

Kind regards,

SebA


On Tue, 29 Jan 2019 at 11:06, Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi,
I am having trouble w.r.t to uptime status generation in clients. The server is displaying uptime correctly since xymond fetches the data, whereas for the clients it does not fetch the uptime data. However it populates all other columns. Can you please suggest if I am missing anything here.

Situation :

Xymon server  and Xymon clients are  configured. The table is populated with colors and data being generated except for uptime in clients whereas the server is reporting uptime correctly. This is probably because of xymond daemon. The status message also indicated service not available which indicates xymond service.  So how can we get the Xymon clients to  update the uptime.

Tasks.cfg file :

# The client back-end module. You need this if you are running the Xymon client on any system.
[clientdata]
        ENVFILE /home/xymon/server/etc/xymonserver.cfg
        NEEDS xymond
        CMD xymond_channel --channel=client --log=$XYMONSERVERLOGS/clientdata.log xymond_client --uptime-status

Status message :

[cid:user-761c62a55bae@xymon.invalid7ADCF0]


Thanks and Regards,
Devvkanth K
Unix SME
list Kii Noda · Fri, 8 Feb 2019 14:25:50 +0200 ·
Hi Devvkanth,

looking at the pic you sent it looks like all you're actually checking on
all machines other than the server is remote checks - conn & ntp. Other
than that, everything is purple so that means that your clients are not
sending their statuses to the xymon server. So please check that and get to
a state where all your checks are either green, yellow, red or white. If
they're purple, it means that you did receive some data in the past but
you're no longer receiving data for those checks. Sample screenshot here:
https://ibb.co/djX5Tzc

As for the uptime check, Xymon's uptime check is bundled within the CPU
check in the UI, although you can alert on it separately. Sample screenshot
here: https://ibb.co/745XLgT

Hope that helps!

On Thu, Feb 7, 2019 at 2:08 PM Devvkanth Krishnamurthy <
▸ quoted from Devvkanth Krishnamurthy
user-8a837177683f@xymon.invalid> wrote:
Hi,


I have removed the uptime from hosts.cfg file and  --uptime-status is
inserted in tasks.cfg. yet I do not see the uptime column in it . Please
check below, I have tried all the resolution available on the net, but I m
not able to figure this one out.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* SebA <user-4631430d620a@xymon.invalid>
*Sent:* Tuesday, February 5, 2019 12:58 AM
*To:* Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* Re: [Xymon] Client uptime status is failing


I've never seen that before - have you added uptime to hosts.cfg?  If so,
remove it!  (It looks like the Xymon server is testing a network service
here, and uptime is not a network service!)


Kind regards,

SebA


On Mon, 4 Feb 2019 at 16:10, Devvkanth Krishnamurthy <
user-8a837177683f@xymon.invalid> wrote:

Hi,


Do you mind giving any suggestions on why only the Xymon server uptime is
reporting correctly whereas the client says that service is unavailable.
Not sure what I am missing here.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* Devvkanth Krishnamurthy
*Sent:* Tuesday, January 29, 2019 5:45 PM
*To:* SebA <user-4631430d620a@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* RE: [Xymon] Client uptime status is failing


Hi,


I have Xymon version – 4.3.28 for both server and clients.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* SebA <user-4631430d620a@xymon.invalid>
*Sent:* Tuesday, January 29, 2019 5:17 PM
*To:* Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* Re: [Xymon] Client uptime status is failing


This may be down to what your clients are reporting.  What client
version(s) are you talking about here?


Kind regards,

SebA


On Tue, 29 Jan 2019 at 11:06, Devvkanth Krishnamurthy <
user-8a837177683f@xymon.invalid> wrote:

Hi,

I am having trouble w.r.t to uptime status generation in clients. The
server is displaying uptime correctly since xymond fetches the data,
whereas for the clients it does not fetch the uptime data. However it
populates all other columns. Can you please suggest if I am missing
anything here.


*Situation* :


Xymon server  and Xymon clients are  configured. The table is populated
with colors and data being generated except for uptime in clients whereas
the server is reporting uptime correctly. This is probably because of
xymond daemon. The status message also indicated service not available
which indicates xymond service.  So how can we get the Xymon clients to
update the uptime.


*Tasks.cfg file :*


# The client back-end module. You need this if you are running the Xymon
client on any system.

[clientdata]

        ENVFILE /home/xymon/server/etc/xymonserver.cfg

        NEEDS xymond

        CMD xymond_channel --channel=client
--log=$XYMONSERVERLOGS/clientdata.log xymond_client --uptime-status


*Status message :*


Thanks and Regards,

Devvkanth K

Unix SME


<https://apac01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.xymon.com%2Fmailman%2Flistinfo%2Fxymon&data=user-77322baadbba@xymon.invalid%7Ce137c43db8144c03f70908d68ad6f818%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636849053246044911&sdata=jp4Km0s7yeEIxZEA716BOnjPCxmvXmL3ZXISYWyMXg4%3D&reserved=0>;

list Devvkanth Krishnamurthy · Fri, 8 Feb 2019 13:57:18 +0000 ·
Hi Kii,

Thanks for the color coding information. As the CPU top command usually reveals the uptime. I am trying to have a separate uptime column which is not showing up as I mentioned below. I will be troubleshooting why the clients are not fetching the data now when it did 3 days back. But uptime column never worked for me. I need it for monitoring as well as uptime report.
▸ quoted from Kii Noda

Thanks and Regards,
Devvkanth K
Unix SME

From: Kii NODA <user-d20081af5452@xymon.invalid>
Sent: Friday, February 8, 2019 5:56 PM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
Cc: SebA <user-4631430d620a@xymon.invalid>; xymon at xymon.com
Subject: Re: [Xymon] Client uptime status is failing

Hi Devvkanth,

looking at the pic you sent it looks like all you're actually checking on all machines other than the server is remote checks - conn & ntp. Other than that, everything is purple so that means that your clients are not sending their statuses to the xymon server. So please check that and get to a state where all your checks are either green, yellow, red or white. If they're purple, it means that you did receive some data in the past but you're no longer receiving data for those checks. Sample screenshot here: https://ibb.co/djX5Tzc<https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fibb.co%2FdjX5Tzc&data=user-77322baadbba@xymon.invalid%7Cb2870accc756491fc6c108d68dc0b47f%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852256146140415&sdata=RYU%2FqMq2LjUDq0tPLu1srY7WH7L4056QalYd1zgABtk%3D&reserved=0>;

As for the uptime check, Xymon's uptime check is bundled within the CPU check in the UI, although you can alert on it separately. Sample screenshot here: https://ibb.co/745XLgT<https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fibb.co%2F745XLgT&data=user-77322baadbba@xymon.invalid%7Cb2870accc756491fc6c108d68dc0b47f%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852256146150425&sdata=wGEoCfHFDWRXBqWBB1Rh%2FfzVWsqAESZJ05tAnK%2BS2hI%3D&reserved=0>;
▸ quoted from Kii Noda

Hope that helps!

On Thu, Feb 7, 2019 at 2:08 PM Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi,

I have removed the uptime from hosts.cfg file and  --uptime-status is inserted in tasks.cfg. yet I do not see the uptime column in it . Please check below, I have tried all the resolution available on the net, but I m not able to figure this one out.

[cid:image001.png at 01D4BFE4.4B376FC0]
▸ quoted from Kii Noda

Thanks and Regards,
Devvkanth K
Unix SME

From: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>
Sent: Tuesday, February 5, 2019 12:58 AM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>>
Cc: xymon at xymon.com<mailto:xymon at xymon.com>
Subject: Re: [Xymon] Client uptime status is failing

I've never seen that before - have you added uptime to hosts.cfg?  If so, remove it!  (It looks like the Xymon server is testing a network service here, and uptime is not a network service!)

Kind regards,

SebA


On Mon, 4 Feb 2019 at 16:10, Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi,

Do you mind giving any suggestions on why only the Xymon server uptime is reporting correctly whereas the client says that service is unavailable. Not sure what I am missing here.

Thanks and Regards,
Devvkanth K
Unix SME

From: Devvkanth Krishnamurthy
Sent: Tuesday, January 29, 2019 5:45 PM
To: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>
Cc: xymon at xymon.com<mailto:xymon at xymon.com>
Subject: RE: [Xymon] Client uptime status is failing

Hi,

I have Xymon version – 4.3.28 for both server and clients.

Thanks and Regards,
Devvkanth K
Unix SME

From: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>
Sent: Tuesday, January 29, 2019 5:17 PM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>>
Cc: xymon at xymon.com<mailto:xymon at xymon.com>
Subject: Re: [Xymon] Client uptime status is failing

This may be down to what your clients are reporting.  What client version(s) are you talking about here?

Kind regards,

SebA


On Tue, 29 Jan 2019 at 11:06, Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi,
I am having trouble w.r.t to uptime status generation in clients. The server is displaying uptime correctly since xymond fetches the data, whereas for the clients it does not fetch the uptime data. However it populates all other columns. Can you please suggest if I am missing anything here.

Situation :

Xymon server  and Xymon clients are  configured. The table is populated with colors and data being generated except for uptime in clients whereas the server is reporting uptime correctly. This is probably because of xymond daemon. The status message also indicated service not available which indicates xymond service.  So how can we get the Xymon clients to  update the uptime.

Tasks.cfg file :

# The client back-end module. You need this if you are running the Xymon client on any system.
[clientdata]
        ENVFILE /home/xymon/server/etc/xymonserver.cfg
        NEEDS xymond
        CMD xymond_channel --channel=client --log=$XYMONSERVERLOGS/clientdata.log xymond_client --uptime-status

Status message :

[cid:image002.png at 01D4BFE4.4B376FC0]


Thanks and Regards,
Devvkanth K
Unix SME


Xymon at xymon.com<https://apac01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.xymon.com%2Fmailman%2Flistinfo%2Fxymon&data=user-77322baadbba@xymon.invalid%7Cb2870accc756491fc6c108d68dc0b47f%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852256146150425&sdata=yWD8zqPfuKGiGOFoUQAUBPMir1UWjWKDfaCyXHBNljw%3D&reserved=0>;
list Kii Noda · Fri, 8 Feb 2019 17:11:14 +0200 ·
Not sure what your use-case is for such a column but you could then create
a custom check. The URL below should have enough info to get you started.

http://xymon.sourceforge.net/xymon/help/xymon-tips.html#scripts

On Fri, Feb 8, 2019 at 3:57 PM Devvkanth Krishnamurthy <
▸ quoted from Devvkanth Krishnamurthy
user-8a837177683f@xymon.invalid> wrote:
Hi Kii,


Thanks for the color coding information. As the CPU top command usually
reveals the uptime. I am trying to have a separate uptime column which is
not showing up as I mentioned below. I will be troubleshooting why the
clients are not fetching the data now when it did 3 days back. But uptime
column never worked for me. I need it for monitoring as well as uptime
report.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* Kii NODA <user-d20081af5452@xymon.invalid>
*Sent:* Friday, February 8, 2019 5:56 PM
*To:* Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
*Cc:* SebA <user-4631430d620a@xymon.invalid>; xymon at xymon.com
*Subject:* Re: [Xymon] Client uptime status is failing


Hi Devvkanth,


looking at the pic you sent it looks like all you're actually checking on
all machines other than the server is remote checks - conn & ntp. Other
than that, everything is purple so that means that your clients are not
sending their statuses to the xymon server. So please check that and get
to a state where all your checks are either green, yellow, red or white. If
they're purple, it means that you did receive some data in the past but
you're no longer receiving data for those checks. Sample screenshot here:
https://ibb.co/djX5Tzc

<https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fibb.co%2FdjX5Tzc&data=user-77322baadbba@xymon.invalid%7Cb2870accc756491fc6c108d68dc0b47f%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852256146140415&sdata=RYU%2FqMq2LjUDq0tPLu1srY7WH7L4056QalYd1zgABtk%3D&reserved=0>;
▸ quoted from Devvkanth Krishnamurthy


As for the uptime check, Xymon's uptime check is bundled within the CPU
check in the UI, although you can alert on it separately. Sample screenshot
here: https://ibb.co/745XLgT

<https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fibb.co%2F745XLgT&data=user-77322baadbba@xymon.invalid%7Cb2870accc756491fc6c108d68dc0b47f%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852256146150425&sdata=wGEoCfHFDWRXBqWBB1Rh%2FfzVWsqAESZJ05tAnK%2BS2hI%3D&reserved=0>;
▸ signature


Hope that helps!


On Thu, Feb 7, 2019 at 2:08 PM Devvkanth Krishnamurthy <

▸ quoted from Devvkanth Krishnamurthy
user-8a837177683f@xymon.invalid> wrote:

Hi,


I have removed the uptime from hosts.cfg file and  --uptime-status is
inserted in tasks.cfg. yet I do not see the uptime column in it . Please
check below, I have tried all the resolution available on the net, but I m
not able to figure this one out.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* SebA <user-4631430d620a@xymon.invalid>
*Sent:* Tuesday, February 5, 2019 12:58 AM
*To:* Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* Re: [Xymon] Client uptime status is failing


I've never seen that before - have you added uptime to hosts.cfg?  If so,
remove it!  (It looks like the Xymon server is testing a network service
here, and uptime is not a network service!)


Kind regards,

SebA


On Mon, 4 Feb 2019 at 16:10, Devvkanth Krishnamurthy <
user-8a837177683f@xymon.invalid> wrote:

Hi,


Do you mind giving any suggestions on why only the Xymon server uptime is
reporting correctly whereas the client says that service is unavailable.
Not sure what I am missing here.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* Devvkanth Krishnamurthy
*Sent:* Tuesday, January 29, 2019 5:45 PM
*To:* SebA <user-4631430d620a@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* RE: [Xymon] Client uptime status is failing


Hi,


I have Xymon version – 4.3.28 for both server and clients.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* SebA <user-4631430d620a@xymon.invalid>
*Sent:* Tuesday, January 29, 2019 5:17 PM
*To:* Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* Re: [Xymon] Client uptime status is failing


This may be down to what your clients are reporting.  What client
version(s) are you talking about here?


Kind regards,

SebA


On Tue, 29 Jan 2019 at 11:06, Devvkanth Krishnamurthy <
user-8a837177683f@xymon.invalid> wrote:

Hi,

I am having trouble w.r.t to uptime status generation in clients. The
server is displaying uptime correctly since xymond fetches the data,
whereas for the clients it does not fetch the uptime data. However it
populates all other columns. Can you please suggest if I am missing
anything here.


*Situation* :


Xymon server  and Xymon clients are  configured. The table is populated
with colors and data being generated except for uptime in clients whereas
the server is reporting uptime correctly. This is probably because of
xymond daemon. The status message also indicated service not available
which indicates xymond service.  So how can we get the Xymon clients to
update the uptime.


*Tasks.cfg file :*


# The client back-end module. You need this if you are running the Xymon
client on any system.

[clientdata]

        ENVFILE /home/xymon/server/etc/xymonserver.cfg

        NEEDS xymond

        CMD xymond_channel --channel=client
--log=$XYMONSERVERLOGS/clientdata.log xymond_client --uptime-status


*Status message :*


Thanks and Regards,

Devvkanth K

Unix SME


<https://apac01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.xymon.com%2Fmailman%2Flistinfo%2Fxymon&data=user-77322baadbba@xymon.invalid%7Cb2870accc756491fc6c108d68dc0b47f%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852256146150425&sdata=yWD8zqPfuKGiGOFoUQAUBPMir1UWjWKDfaCyXHBNljw%3D&reserved=0>;


<https://apac01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.xymon.com%2Fmailman%2Flistinfo%2Fxymon&data=user-77322baadbba@xymon.invalid%7Cb2870accc756491fc6c108d68dc0b47f%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852256146160434&sdata=6X7uXGsuCpNkgTf3G3HnJVG946rFpRop0lvrYqYzN%2Fg%3D&reserved=0>;

list Sebastian Auriol · Fri, 8 Feb 2019 18:00:36 +0000 ·
Client don't fetch data unless you're using xymon-rclient - they report
data.  It could be being reported to the wrong IP address or port, or
blocked in a firewall, although given that one of them is your Xymon
server, probably not!  You could run tcpdump on port 1984 on the xymon
server to see the reports coming in, or lack of them.

After your original e-mail, I actually took what you had added to tasks.cfg
and added it to mine and uptime instantly appeared as a new column on my
display (by the time I'd looked at the page).  So there is nothing wrong
with your syntax.

Kind regards,

SebA


On Fri, 8 Feb 2019 at 13:57, Devvkanth Krishnamurthy <
▸ quoted from Kii Noda
user-8a837177683f@xymon.invalid> wrote:
Hi Kii,


Thanks for the color coding information. As the CPU top command usually
reveals the uptime. I am trying to have a separate uptime column which is
not showing up as I mentioned below. I will be troubleshooting why the
clients are not fetching the data now when it did 3 days back. But uptime
column never worked for me. I need it for monitoring as well as uptime
report.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* Kii NODA <user-d20081af5452@xymon.invalid>
*Sent:* Friday, February 8, 2019 5:56 PM
*To:* Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
*Cc:* SebA <user-4631430d620a@xymon.invalid>; xymon at xymon.com
*Subject:* Re: [Xymon] Client uptime status is failing


Hi Devvkanth,


looking at the pic you sent it looks like all you're actually checking on
all machines other than the server is remote checks - conn & ntp. Other
than that, everything is purple so that means that your clients are not
sending their statuses to the xymon server. So please check that and get
to a state where all your checks are either green, yellow, red or white. If
they're purple, it means that you did receive some data in the past but
you're no longer receiving data for those checks. Sample screenshot here:
https://ibb.co/djX5Tzc
<https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fibb.co%2FdjX5Tzc&data=user-77322baadbba@xymon.invalid%7Cb2870accc756491fc6c108d68dc0b47f%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852256146140415&sdata=RYU%2FqMq2LjUDq0tPLu1srY7WH7L4056QalYd1zgABtk%3D&reserved=0>;


As for the uptime check, Xymon's uptime check is bundled within the CPU
check in the UI, although you can alert on it separately. Sample screenshot
here: https://ibb.co/745XLgT
<https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fibb.co%2F745XLgT&data=user-77322baadbba@xymon.invalid%7Cb2870accc756491fc6c108d68dc0b47f%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852256146150425&sdata=wGEoCfHFDWRXBqWBB1Rh%2FfzVWsqAESZJ05tAnK%2BS2hI%3D&reserved=0>;


Hope that helps!


On Thu, Feb 7, 2019 at 2:08 PM Devvkanth Krishnamurthy <
user-8a837177683f@xymon.invalid> wrote:

Hi,


I have removed the uptime from hosts.cfg file and  --uptime-status is
inserted in tasks.cfg. yet I do not see the uptime column in it . Please
check below, I have tried all the resolution available on the net, but I m
not able to figure this one out.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* SebA <user-4631430d620a@xymon.invalid>
*Sent:* Tuesday, February 5, 2019 12:58 AM
*To:* Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* Re: [Xymon] Client uptime status is failing


I've never seen that before - have you added uptime to hosts.cfg?  If so,
remove it!  (It looks like the Xymon server is testing a network service
here, and uptime is not a network service!)


Kind regards,

SebA


On Mon, 4 Feb 2019 at 16:10, Devvkanth Krishnamurthy <
user-8a837177683f@xymon.invalid> wrote:

Hi,


Do you mind giving any suggestions on why only the Xymon server uptime is
reporting correctly whereas the client says that service is unavailable.
Not sure what I am missing here.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* Devvkanth Krishnamurthy
*Sent:* Tuesday, January 29, 2019 5:45 PM
*To:* SebA <user-4631430d620a@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* RE: [Xymon] Client uptime status is failing


Hi,


I have Xymon version – 4.3.28 for both server and clients.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* SebA <user-4631430d620a@xymon.invalid>
*Sent:* Tuesday, January 29, 2019 5:17 PM
*To:* Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* Re: [Xymon] Client uptime status is failing


This may be down to what your clients are reporting.  What client
version(s) are you talking about here?


Kind regards,

SebA


On Tue, 29 Jan 2019 at 11:06, Devvkanth Krishnamurthy <
user-8a837177683f@xymon.invalid> wrote:

Hi,

I am having trouble w.r.t to uptime status generation in clients. The
server is displaying uptime correctly since xymond fetches the data,
whereas for the clients it does not fetch the uptime data. However it
populates all other columns. Can you please suggest if I am missing
anything here.


*Situation* :


Xymon server  and Xymon clients are  configured. The table is populated
with colors and data being generated except for uptime in clients whereas
the server is reporting uptime correctly. This is probably because of
xymond daemon. The status message also indicated service not available
which indicates xymond service.  So how can we get the Xymon clients to
update the uptime.


*Tasks.cfg file :*


# The client back-end module. You need this if you are running the Xymon
client on any system.

[clientdata]

        ENVFILE /home/xymon/server/etc/xymonserver.cfg

        NEEDS xymond

        CMD xymond_channel --channel=client
--log=$XYMONSERVERLOGS/clientdata.log xymond_client --uptime-status


*Status message :*


Thanks and Regards,

Devvkanth K

Unix SME


<https://apac01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.xymon.com%2Fmailman%2Flistinfo%2Fxymon&data=user-77322baadbba@xymon.invalid%7Cb2870accc756491fc6c108d68dc0b47f%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852256146150425&sdata=yWD8zqPfuKGiGOFoUQAUBPMir1UWjWKDfaCyXHBNljw%3D&reserved=0>;


<https://apac01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.xymon.com%2Fmailman%2Flistinfo%2Fxymon&data=user-77322baadbba@xymon.invalid%7Cb2870accc756491fc6c108d68dc0b47f%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852256146160434&sdata=6X7uXGsuCpNkgTf3G3HnJVG946rFpRop0lvrYqYzN%2Fg%3D&reserved=0>;

list Devvkanth Krishnamurthy · Fri, 8 Feb 2019 18:12:53 +0000 ·
Hi Kii/SebA ,

I was able to see the uptime appear in the main view. For both of those servers that are showing correctly, reinstallation worked. But I can’t understand why. Is there any parameters that we need to consider before installing the clients ? Still I have to check the purple ones and the Xymon server itself is showing in purple.

But I need to scan the port 1984 as well. I will update as I work on this.

[cid:image001.jpg at 01D4C008.0054DD20]
▸ quoted from Sebastian Auriol

Thanks and Regards,
Devvkanth K
Unix SME

From: SebA <user-4631430d620a@xymon.invalid>
Sent: Friday, February 8, 2019 11:31 PM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
Cc: Kii NODA <user-d20081af5452@xymon.invalid>; xymon at xymon.com
Subject: Re: [Xymon] Client uptime status is failing

Client don't fetch data unless you're using xymon-rclient - they report data.  It could be being reported to the wrong IP address or port, or blocked in a firewall, although given that one of them is your Xymon server, probably not!  You could run tcpdump on port 1984 on the xymon server to see the reports coming in, or lack of them.

After your original e-mail, I actually took what you had added to tasks.cfg and added it to mine and uptime instantly appeared as a new column on my display (by the time I'd looked at the page).  So there is nothing wrong with your syntax.

Kind regards,

SebA


On Fri, 8 Feb 2019 at 13:57, Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi Kii,

Thanks for the color coding information. As the CPU top command usually reveals the uptime. I am trying to have a separate uptime column which is not showing up as I mentioned below. I will be troubleshooting why the clients are not fetching the data now when it did 3 days back. But uptime column never worked for me. I need it for monitoring as well as uptime report.

Thanks and Regards,
Devvkanth K
Unix SME

From: Kii NODA <user-d20081af5452@xymon.invalid<mailto:user-d20081af5452@xymon.invalid>>
Sent: Friday, February 8, 2019 5:56 PM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>>
Cc: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>; xymon at xymon.com<mailto:xymon at xymon.com>
Subject: Re: [Xymon] Client uptime status is failing

Hi Devvkanth,

looking at the pic you sent it looks like all you're actually checking on all machines other than the server is remote checks - conn & ntp. Other than that, everything is purple so that means that your clients are not sending their statuses to the xymon server. So please check that and get to a state where all your checks are either green, yellow, red or white. If they're purple, it means that you did receive some data in the past but you're no longer receiving data for those checks. Sample screenshot here: https://ibb.co/djX5Tzc<https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fibb.co%2FdjX5Tzc&data=user-77322baadbba@xymon.invalid%7C643dcffe0e244a6bd4cb08d68def82b5%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852457482010890&sdata=y0G8izJYBVQZUDpXfoSK0SrJhO8CdfR7q3cLlYrXGVg%3D&reserved=0>;

As for the uptime check, Xymon's uptime check is bundled within the CPU check in the UI, although you can alert on it separately. Sample screenshot here: https://ibb.co/745XLgT<https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fibb.co%2F745XLgT&data=user-77322baadbba@xymon.invalid%7C643dcffe0e244a6bd4cb08d68def82b5%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852457482020895&sdata=60sUqkTclPc56Fz3tJKY2HCdS9lCzXUaFcXhHylAyQc%3D&reserved=0>;
▸ quoted from Sebastian Auriol

Hope that helps!

On Thu, Feb 7, 2019 at 2:08 PM Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi,

I have removed the uptime from hosts.cfg file and  --uptime-status is inserted in tasks.cfg. yet I do not see the uptime column in it . Please check below, I have tried all the resolution available on the net, but I m not able to figure this one out.

[cid:image003.png at 01D4C007.A2DD4060]
▸ quoted from Sebastian Auriol

Thanks and Regards,
Devvkanth K
Unix SME

From: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>
Sent: Tuesday, February 5, 2019 12:58 AM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>>
Cc: xymon at xymon.com<mailto:xymon at xymon.com>
Subject: Re: [Xymon] Client uptime status is failing

I've never seen that before - have you added uptime to hosts.cfg?  If so, remove it!  (It looks like the Xymon server is testing a network service here, and uptime is not a network service!)

Kind regards,

SebA


On Mon, 4 Feb 2019 at 16:10, Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi,

Do you mind giving any suggestions on why only the Xymon server uptime is reporting correctly whereas the client says that service is unavailable. Not sure what I am missing here.

Thanks and Regards,
Devvkanth K
Unix SME

From: Devvkanth Krishnamurthy
Sent: Tuesday, January 29, 2019 5:45 PM
To: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>
Cc: xymon at xymon.com<mailto:xymon at xymon.com>
Subject: RE: [Xymon] Client uptime status is failing

Hi,

I have Xymon version – 4.3.28 for both server and clients.

Thanks and Regards,
Devvkanth K
Unix SME

From: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>
Sent: Tuesday, January 29, 2019 5:17 PM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>>
Cc: xymon at xymon.com<mailto:xymon at xymon.com>
Subject: Re: [Xymon] Client uptime status is failing

This may be down to what your clients are reporting.  What client version(s) are you talking about here?

Kind regards,

SebA


On Tue, 29 Jan 2019 at 11:06, Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi,
I am having trouble w.r.t to uptime status generation in clients. The server is displaying uptime correctly since xymond fetches the data, whereas for the clients it does not fetch the uptime data. However it populates all other columns. Can you please suggest if I am missing anything here.

Situation :

Xymon server  and Xymon clients are  configured. The table is populated with colors and data being generated except for uptime in clients whereas the server is reporting uptime correctly. This is probably because of xymond daemon. The status message also indicated service not available which indicates xymond service.  So how can we get the Xymon clients to  update the uptime.

Tasks.cfg file :

# The client back-end module. You need this if you are running the Xymon client on any system.
[clientdata]
        ENVFILE /home/xymon/server/etc/xymonserver.cfg
        NEEDS xymond
        CMD xymond_channel --channel=client --log=$XYMONSERVERLOGS/clientdata.log xymond_client --uptime-status

Status message :

[cid:image004.png at 01D4C007.A2DD4060]


Thanks and Regards,
Devvkanth K
Unix SME


Xymon at xymon.com<https://apac01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.xymon.com%2Fmailman%2Flistinfo%2Fxymon&data=user-77322baadbba@xymon.invalid%7C643dcffe0e244a6bd4cb08d68def82b5%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852457482030909&sdata=bD7N4mAOqw4ObKM%2B6qrI8mWtIGL5v9Mna6827XZBKDs%3D&reserved=0>;
Attachments (1)
list Sebastian Auriol · Fri, 8 Feb 2019 18:18:03 +0000 ·
You can check the Ghosts report.  The client name needs to match either the
main name in hosts.cfg or the CLIENTNAME tag in hosts.cfg.  It may that
they are reporting, but not matching a host and so being listed as a ghost
instead.

Kind regards,

SebA


On Fri, 8 Feb 2019 at 18:13, Devvkanth Krishnamurthy <
▸ quoted from Devvkanth Krishnamurthy
user-8a837177683f@xymon.invalid> wrote:
Hi Kii/SebA ,


I was able to see the uptime appear in the main view. For both of those
servers that are showing correctly, reinstallation worked. But I can’t
understand why. Is there any parameters that we need to consider before
installing the clients ? Still I have to check the purple ones and the
Xymon server itself is showing in purple.


But I need to scan the port 1984 as well. I will update as I work on this.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* SebA <user-4631430d620a@xymon.invalid>
*Sent:* Friday, February 8, 2019 11:31 PM
*To:* Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
*Cc:* Kii NODA <user-d20081af5452@xymon.invalid>; xymon at xymon.com
*Subject:* Re: [Xymon] Client uptime status is failing


Client don't fetch data unless you're using xymon-rclient - they report
data.  It could be being reported to the wrong IP address or port, or
blocked in a firewall, although given that one of them is your Xymon
server, probably not!  You could run tcpdump on port 1984 on the xymon
server to see the reports coming in, or lack of them.


After your original e-mail, I actually took what you had added to
tasks.cfg and added it to mine and uptime instantly appeared as a new
column on my display (by the time I'd looked at the page).  So there is
nothing wrong with your syntax.


Kind regards,

SebA


On Fri, 8 Feb 2019 at 13:57, Devvkanth Krishnamurthy <
user-8a837177683f@xymon.invalid> wrote:

Hi Kii,


Thanks for the color coding information. As the CPU top command usually
reveals the uptime. I am trying to have a separate uptime column which is
not showing up as I mentioned below. I will be troubleshooting why the
clients are not fetching the data now when it did 3 days back. But uptime
column never worked for me. I need it for monitoring as well as uptime
report.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* Kii NODA <user-d20081af5452@xymon.invalid>
*Sent:* Friday, February 8, 2019 5:56 PM
*To:* Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
*Cc:* SebA <user-4631430d620a@xymon.invalid>; xymon at xymon.com
*Subject:* Re: [Xymon] Client uptime status is failing


Hi Devvkanth,


looking at the pic you sent it looks like all you're actually checking on
all machines other than the server is remote checks - conn & ntp. Other
than that, everything is purple so that means that your clients are not
sending their statuses to the xymon server. So please check that and get
to a state where all your checks are either green, yellow, red or white. If
they're purple, it means that you did receive some data in the past but
you're no longer receiving data for those checks. Sample screenshot here:
https://ibb.co/djX5Tzc

<https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fibb.co%2FdjX5Tzc&data=user-77322baadbba@xymon.invalid%7C643dcffe0e244a6bd4cb08d68def82b5%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852457482010890&sdata=y0G8izJYBVQZUDpXfoSK0SrJhO8CdfR7q3cLlYrXGVg%3D&reserved=0>;
▸ quoted from Devvkanth Krishnamurthy


As for the uptime check, Xymon's uptime check is bundled within the CPU
check in the UI, although you can alert on it separately. Sample screenshot
here: https://ibb.co/745XLgT

<https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fibb.co%2F745XLgT&data=user-77322baadbba@xymon.invalid%7C643dcffe0e244a6bd4cb08d68def82b5%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852457482020895&sdata=60sUqkTclPc56Fz3tJKY2HCdS9lCzXUaFcXhHylAyQc%3D&reserved=0>;
▸ quoted from Devvkanth Krishnamurthy


Hope that helps!


On Thu, Feb 7, 2019 at 2:08 PM Devvkanth Krishnamurthy <
user-8a837177683f@xymon.invalid> wrote:

Hi,


I have removed the uptime from hosts.cfg file and  --uptime-status is
inserted in tasks.cfg. yet I do not see the uptime column in it . Please
check below, I have tried all the resolution available on the net, but I m
not able to figure this one out.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* SebA <user-4631430d620a@xymon.invalid>
*Sent:* Tuesday, February 5, 2019 12:58 AM
*To:* Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* Re: [Xymon] Client uptime status is failing


I've never seen that before - have you added uptime to hosts.cfg?  If so,
remove it!  (It looks like the Xymon server is testing a network service
here, and uptime is not a network service!)


Kind regards,

SebA


On Mon, 4 Feb 2019 at 16:10, Devvkanth Krishnamurthy <
user-8a837177683f@xymon.invalid> wrote:

Hi,


Do you mind giving any suggestions on why only the Xymon server uptime is
reporting correctly whereas the client says that service is unavailable.
Not sure what I am missing here.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* Devvkanth Krishnamurthy
*Sent:* Tuesday, January 29, 2019 5:45 PM
*To:* SebA <user-4631430d620a@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* RE: [Xymon] Client uptime status is failing


Hi,


I have Xymon version – 4.3.28 for both server and clients.


Thanks and Regards,

Devvkanth K

Unix SME


*From:* SebA <user-4631430d620a@xymon.invalid>
*Sent:* Tuesday, January 29, 2019 5:17 PM
*To:* Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
*Cc:* xymon at xymon.com
*Subject:* Re: [Xymon] Client uptime status is failing


This may be down to what your clients are reporting.  What client
version(s) are you talking about here?


Kind regards,

SebA


On Tue, 29 Jan 2019 at 11:06, Devvkanth Krishnamurthy <
user-8a837177683f@xymon.invalid> wrote:

Hi,

I am having trouble w.r.t to uptime status generation in clients. The
server is displaying uptime correctly since xymond fetches the data,
whereas for the clients it does not fetch the uptime data. However it
populates all other columns. Can you please suggest if I am missing
anything here.


*Situation* :


Xymon server  and Xymon clients are  configured. The table is populated
with colors and data being generated except for uptime in clients whereas
the server is reporting uptime correctly. This is probably because of
xymond daemon. The status message also indicated service not available
which indicates xymond service.  So how can we get the Xymon clients to
update the uptime.


*Tasks.cfg file :*


# The client back-end module. You need this if you are running the Xymon
client on any system.

[clientdata]

        ENVFILE /home/xymon/server/etc/xymonserver.cfg

        NEEDS xymond

        CMD xymond_channel --channel=client
--log=$XYMONSERVERLOGS/clientdata.log xymond_client --uptime-status


*Status message :*


Thanks and Regards,

Devvkanth K

Unix SME


<https://apac01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.xymon.com%2Fmailman%2Flistinfo%2Fxymon&data=user-77322baadbba@xymon.invalid%7C643dcffe0e244a6bd4cb08d68def82b5%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852457482030909&sdata=bD7N4mAOqw4ObKM%2B6qrI8mWtIGL5v9Mna6827XZBKDs%3D&reserved=0>;


<https://apac01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.xymon.com%2Fmailman%2Flistinfo%2Fxymon&data=user-77322baadbba@xymon.invalid%7C643dcffe0e244a6bd4cb08d68def82b5%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852457482030909&sdata=bD7N4mAOqw4ObKM%2B6qrI8mWtIGL5v9Mna6827XZBKDs%3D&reserved=0>;

list Devvkanth Krishnamurthy · Fri, 8 Feb 2019 18:32:38 +0000 ·
Hi,

Port 1984 is listening. I don’t see any clients in Ghost. I am trying to  troubleshoot by using another client and see if it works.

Thanks and Regards,
Devvkanth
▸ quoted from Sebastian Auriol
Unix SME

From: SebA <user-4631430d620a@xymon.invalid>
Sent: Friday, February 8, 2019 11:48 PM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid>
Cc: Kii NODA <user-d20081af5452@xymon.invalid>; xymon at xymon.com
Subject: Re: [Xymon] Client uptime status is failing

You can check the Ghosts report.  The client name needs to match either the main name in hosts.cfg or the CLIENTNAME tag in hosts.cfg.  It may that they are reporting, but not matching a host and so being listed as a ghost instead.

Kind regards,

SebA


On Fri, 8 Feb 2019 at 18:13, Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi Kii/SebA ,

I was able to see the uptime appear in the main view. For both of those servers that are showing correctly, reinstallation worked. But I can’t understand why. Is there any parameters that we need to consider before installing the clients ? Still I have to check the purple ones and the Xymon server itself is showing in purple.

But I need to scan the port 1984 as well. I will update as I work on this.

[cid:image001.jpg at 01D4C009.A257AAC0]
▸ quoted from Sebastian Auriol

Thanks and Regards,
Devvkanth K
Unix SME

From: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>
Sent: Friday, February 8, 2019 11:31 PM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>>
Cc: Kii NODA <user-d20081af5452@xymon.invalid<mailto:user-d20081af5452@xymon.invalid>>; xymon at xymon.com<mailto:xymon at xymon.com>
Subject: Re: [Xymon] Client uptime status is failing

Client don't fetch data unless you're using xymon-rclient - they report data.  It could be being reported to the wrong IP address or port, or blocked in a firewall, although given that one of them is your Xymon server, probably not!  You could run tcpdump on port 1984 on the xymon server to see the reports coming in, or lack of them.

After your original e-mail, I actually took what you had added to tasks.cfg and added it to mine and uptime instantly appeared as a new column on my display (by the time I'd looked at the page).  So there is nothing wrong with your syntax.

Kind regards,

SebA


On Fri, 8 Feb 2019 at 13:57, Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi Kii,

Thanks for the color coding information. As the CPU top command usually reveals the uptime. I am trying to have a separate uptime column which is not showing up as I mentioned below. I will be troubleshooting why the clients are not fetching the data now when it did 3 days back. But uptime column never worked for me. I need it for monitoring as well as uptime report.

Thanks and Regards,
Devvkanth K
Unix SME

From: Kii NODA <user-d20081af5452@xymon.invalid<mailto:user-d20081af5452@xymon.invalid>>
Sent: Friday, February 8, 2019 5:56 PM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>>
Cc: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>; xymon at xymon.com<mailto:xymon at xymon.com>
Subject: Re: [Xymon] Client uptime status is failing

Hi Devvkanth,

looking at the pic you sent it looks like all you're actually checking on all machines other than the server is remote checks - conn & ntp. Other than that, everything is purple so that means that your clients are not sending their statuses to the xymon server. So please check that and get to a state where all your checks are either green, yellow, red or white. If they're purple, it means that you did receive some data in the past but you're no longer receiving data for those checks. Sample screenshot here: https://ibb.co/djX5Tzc<https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fibb.co%2FdjX5Tzc&data=user-77322baadbba@xymon.invalid%7C60c16639798c4cd620f608d68df1e9d3%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852467514360832&sdata=v9oBMfSWAi8x2%2BEM6w%2BR4vYk64N%2Fre1yfpSWmB2tUlY%3D&reserved=0>;

As for the uptime check, Xymon's uptime check is bundled within the CPU check in the UI, although you can alert on it separately. Sample screenshot here: https://ibb.co/745XLgT<https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fibb.co%2F745XLgT&data=user-77322baadbba@xymon.invalid%7C60c16639798c4cd620f608d68df1e9d3%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852467514360832&sdata=SAyfZINNZRu6lyikTsSvZI1ds%2Bp3ezaue5xUtG9DMYg%3D&reserved=0>;
▸ quoted from Sebastian Auriol

Hope that helps!

On Thu, Feb 7, 2019 at 2:08 PM Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi,

I have removed the uptime from hosts.cfg file and  --uptime-status is inserted in tasks.cfg. yet I do not see the uptime column in it . Please check below, I have tried all the resolution available on the net, but I m not able to figure this one out.

[cid:image002.png at 01D4C009.A257AAC0]
▸ quoted from Sebastian Auriol

Thanks and Regards,
Devvkanth K
Unix SME

From: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>
Sent: Tuesday, February 5, 2019 12:58 AM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>>
Cc: xymon at xymon.com<mailto:xymon at xymon.com>
Subject: Re: [Xymon] Client uptime status is failing

I've never seen that before - have you added uptime to hosts.cfg?  If so, remove it!  (It looks like the Xymon server is testing a network service here, and uptime is not a network service!)

Kind regards,

SebA


On Mon, 4 Feb 2019 at 16:10, Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi,

Do you mind giving any suggestions on why only the Xymon server uptime is reporting correctly whereas the client says that service is unavailable. Not sure what I am missing here.

Thanks and Regards,
Devvkanth K
Unix SME

From: Devvkanth Krishnamurthy
Sent: Tuesday, January 29, 2019 5:45 PM
To: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>
Cc: xymon at xymon.com<mailto:xymon at xymon.com>
Subject: RE: [Xymon] Client uptime status is failing

Hi,

I have Xymon version – 4.3.28 for both server and clients.

Thanks and Regards,
Devvkanth K
Unix SME

From: SebA <user-4631430d620a@xymon.invalid<mailto:user-4631430d620a@xymon.invalid>>
Sent: Tuesday, January 29, 2019 5:17 PM
To: Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>>
Cc: xymon at xymon.com<mailto:xymon at xymon.com>
Subject: Re: [Xymon] Client uptime status is failing

This may be down to what your clients are reporting.  What client version(s) are you talking about here?

Kind regards,

SebA


On Tue, 29 Jan 2019 at 11:06, Devvkanth Krishnamurthy <user-8a837177683f@xymon.invalid<mailto:user-8a837177683f@xymon.invalid>> wrote:
Hi,
I am having trouble w.r.t to uptime status generation in clients. The server is displaying uptime correctly since xymond fetches the data, whereas for the clients it does not fetch the uptime data. However it populates all other columns. Can you please suggest if I am missing anything here.

Situation :

Xymon server  and Xymon clients are  configured. The table is populated with colors and data being generated except for uptime in clients whereas the server is reporting uptime correctly. This is probably because of xymond daemon. The status message also indicated service not available which indicates xymond service.  So how can we get the Xymon clients to  update the uptime.

Tasks.cfg file :

# The client back-end module. You need this if you are running the Xymon client on any system.
[clientdata]
        ENVFILE /home/xymon/server/etc/xymonserver.cfg
        NEEDS xymond
        CMD xymond_channel --channel=client --log=$XYMONSERVERLOGS/clientdata.log xymond_client --uptime-status

Status message :

[cid:image003.png at 01D4C009.A257AAC0]


Thanks and Regards,
Devvkanth K
Unix SME


Xymon at xymon.com<https://apac01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.xymon.com%2Fmailman%2Flistinfo%2Fxymon&data=user-77322baadbba@xymon.invalid%7C60c16639798c4cd620f608d68df1e9d3%7C63ce7d592f3e42cda8ccbe764cff5eb6%7C1%7C0%7C636852467514370841&sdata=qZ6hqwzptiPzXG4nVk2NEE7AQcbLaBEXg46CTsB28Go%3D&reserved=0>;